Two duplex receptacles are installed in a double-gang box. The total minimum receptacle load for all receptacles is what value in VA?

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

Two duplex receptacles are installed in a double-gang box. The total minimum receptacle load for all receptacles is what value in VA?

Explanation:
In dwelling-unit load calculations, each receptacle outlet is assumed to have a fixed load of 180 VA, regardless of the actual devices plugged in. A duplex receptacle is counted as one receptacle outlet. With two duplex receptacles in a double-gang box, you have two receptacle outlets: 2 × 180 VA = 360 VA. This is the minimum receptacle load the calculation uses; actual usage can vary, but the fixed 360 VA is the standard basis for sizing.

In dwelling-unit load calculations, each receptacle outlet is assumed to have a fixed load of 180 VA, regardless of the actual devices plugged in. A duplex receptacle is counted as one receptacle outlet. With two duplex receptacles in a double-gang box, you have two receptacle outlets: 2 × 180 VA = 360 VA. This is the minimum receptacle load the calculation uses; actual usage can vary, but the fixed 360 VA is the standard basis for sizing.