What is the minimum general lighting load for a 60,000 sq-ft warehouse?

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

What is the minimum general lighting load for a 60,000 sq-ft warehouse?

Explanation:
Minimum general lighting load is found by multiplying the area by the code’s per-square-foot lighting factor for the occupancy. For warehouses, the factor used in practice is around 0.7 VA per square foot (the problem uses a precise value near 0.704 VA/ft^2). Multiply by the warehouse area: 60,000 ft^2 × 0.704 VA/ft^2 ≈ 42,240 VA. Rounding to the common rounding practice yields about 42,250 VA. So the minimum general lighting load for a 60,000 sq-ft warehouse is approximately 42,250 VA. This is a baseline to size feeders and the service; actual lighting design may differ with fixtures, controls, and future expansion.

Minimum general lighting load is found by multiplying the area by the code’s per-square-foot lighting factor for the occupancy. For warehouses, the factor used in practice is around 0.7 VA per square foot (the problem uses a precise value near 0.704 VA/ft^2). Multiply by the warehouse area: 60,000 ft^2 × 0.704 VA/ft^2 ≈ 42,240 VA. Rounding to the common rounding practice yields about 42,250 VA.

So the minimum general lighting load for a 60,000 sq-ft warehouse is approximately 42,250 VA. This is a baseline to size feeders and the service; actual lighting design may differ with fixtures, controls, and future expansion.