What is the minimum size of the ungrounded conductors in each conduit feeding Panel A?

Prepare for the Independent Electrical Contractors (IEC) Year 4 Exam. Access flashcards, multiple choice questions, and detailed explanations. Enhance your readiness and achieve your certification!

Multiple Choice

What is the minimum size of the ungrounded conductors in each conduit feeding Panel A?

Explanation:
The main idea is sizing feeder conductors to match the panel’s rating using the conductor ampacity in the 75°C column for copper in conduit. If Panel A is fed by a 200-amp feeder, the ungrounded conductors in each conduit must have an ampacity of at least 200 A. Looking at common copper sizes with THHN insulation in the 75°C column, 2/0 AWG is about 115 A, 4 AWG is about 85 A, 4/0 AWG is about 230 A, and 3/0 AWG is around 200 A. So 3/0 copper is the smallest size that meets the 200 A requirement. That’s why 3/0 copper is the correct minimum. Larger sizes like 4/0 are allowed but not the minimum, and smaller sizes would not suffice for a 200 A feeder.

The main idea is sizing feeder conductors to match the panel’s rating using the conductor ampacity in the 75°C column for copper in conduit. If Panel A is fed by a 200-amp feeder, the ungrounded conductors in each conduit must have an ampacity of at least 200 A. Looking at common copper sizes with THHN insulation in the 75°C column, 2/0 AWG is about 115 A, 4 AWG is about 85 A, 4/0 AWG is about 230 A, and 3/0 AWG is around 200 A. So 3/0 copper is the smallest size that meets the 200 A requirement. That’s why 3/0 copper is the correct minimum. Larger sizes like 4/0 are allowed but not the minimum, and smaller sizes would not suffice for a 200 A feeder.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy